we r using philips 89c669 ,in design we r using DS1232
to provide reset to 89C669.
Reset doesnt come up most of the time.

Is this problem of microcontroller?

Parents
  • Have you used the correct reset signal? The DS1232 has one open-drain active-low reset signal, and one push-pull active high signal.

    Have you looked at the reset signal? Does it leave the reset state 250ms after power has reached correct values? Will the supply voltage ever reach correct values?

Reply
  • Have you used the correct reset signal? The DS1232 has one open-drain active-low reset signal, and one push-pull active high signal.

    Have you looked at the reset signal? Does it leave the reset state 250ms after power has reached correct values? Will the supply voltage ever reach correct values?