About transferring 4-20mA to voltage

Dear friends,

I am working on reading 4-20 mA from Level/pressure/flow transmitters.
I used to use a 10 ohm resistor in series. so I measured the voltage drop on the resistor
but in this circuit I needed the ground from the transmitter device.
Is there a better method not using ground wire from the transmitter?

Parents Reply Children
  • Sorry, but I do not understand you.

    An OP-amp has two inputs and can work with differential data. But both the inputs and the output(s) needs to be slightly inside the supply range of the OP-amp.

    So the cost/complexity of your design will increase if you need full isolation.

    One solution is to use a linear optocoupler where the current is used to modulate the LED.

    Another is to have a voltage-controlled-oscillator feeding a transformer and pick up the frequency on the other winding.

    A third is to send the current through a coil and use a Hall effect sensor to measure the strength of the produced magnetic field.

    Yet another option is to isolate your measurement device - then you can send the current through a resistor and directly measure the voltage. Then you use whatever isolation you need in the next step - forwarding the measured value. Power supplies are isolated, just as 10base-T, 100base-T, ... Ethernet connectors, making it easy with a single input forwarded over Ethernet.

    Or open the wallet and spend some money on something like:
    www.fine-tek.com/.../pinfo_in.aspx